Bill Turax
- MD
We are installing a 600 amp residential service with a CT cabinet.
there are (3) 200 amp service disconnects. each disconnect is fed with 2/0 CU and the load side has 4/0 AL.
the issue is with the GEC to the cold water pipe. we installed (3) pieces of #4 CU to the cold water, 1 piece from each disconnect. the inspector says we need (1) piece of 1/0 CU or 3/0 AL.
I understand this comes from 250.66 (3 pieces of 4/0 = 635 KCMIL), the chart says this would be 1/0 CU or 3/0 AL. however we are taking a #4 from each disconnect separately so the largest ungrounded conductor in the disconnect is 4/0 AL and per 250.66 that only needs to be a #4 CU.
when installing a 400 amp residential service with (2) disconnects with 4/0 AL w always use (2) pieces of #4 CU for the water GEC and have never had an issue. why would it be different for the 600 amp service with an additional disconnect and #4 GEC?