M. D. said:As the temp of the wire increases so does the resistance more resistance equals more heat which adds to the resistance again creating more heat,.. and with this not being sized at 125% it could indeed trip.
Also the manufacturer rates the elements at a nominal voltage . Sometimes a wattage at 208 and 230 . If you have 240 volts or a little over and subject to power surges, and the breaker is already hot from being borderline it will trip for sure.