Hello All. I noticed at one of my surveys that a rated 240V 4.5KW water heater single phase has a 2-pole 30AMP breaker, which is fine. But the panel voltage is 208V. Shouldn't it technically be a 25A breaker for 208V since the power of the water heater now 3.3KW? I don't see it as being a problem since the cable is a #10 copper capable for 30Amp. But is this considered a violation? Thanks!
The water heater cutsheet model does not give a FLA or circuit breaker size, just that is rated for 4.5KW and is capable of doing 208V also.