clsarmiento
Member
What's the correct amps load for a 4.5KW, 2-element (non-simultaneous operation), 480volt, 3-phase electric water heater?
Thanks.
Thanks.
Hi !!
4.5 KW , 480V 3 phase heater .
Thus , the current will be 5.41 Amperes .
Transient
So called 3 phase water heating elements certainly exist, I have one in front of me.
They consist of 3 elements assembled in the same housing housing, with either 3 or 4 terminals according to design.
What's the correct amps load for a 4.5KW, 2-element (non-simultaneous operation), 480volt, 3-phase electric water heater?
Thanks.
no need so much brain storming ,
just need to know how much the total current will be drawn by an euipment which is 4.5KW rated , 480V .
So , the answer is 5.41 amps .
For those , who have not seen 3 phase elements , its not my fault .
Transient.
Your answer is correct.
4500 happens to be most common size for household tank style water heaters but is generally single phase 240 volts. I think people are getting too hung up on that instead of looking at the question. But at this site we are really good at picking apart things and occasionally do make fools of ourselves when we run into something not too common, other times we catch a person not fully understanding what they have.
I looked at the question I just questioned the question.Once I realized it may be a test question and they make 3 phase 4500 watt elements then I agree with the answers given
Out of curiosity, why do you guys call current Amperage?
Typically an electric water heater has two similar elements, the lower one cuts in when the incoming cold water reduces the temperature at its thermostat. The top element cuts in when the water which is going to be output from the tank goes below the set temperature.The OP states there are two elements. These two elements share a common leg. Is this three phase open delta?
Out of curiosity, why do you guys call current Amperage?
.
Bottom line: If both elements were three phase, it could be wye, or either open or closed delta, and the thermostat would be triple pole or a contractor would be used. They need not share a common leg.
Why even consider non-simultaneous operation of such a small load. Even with simultaneous operation, this is less than 12 amps total load. Most places I have been don't allow power wiring below #12 is allowed anyway, regardless of the actual load. (Not code, but owner rule. Assume this is some kind of industrial installation since it's 3 phase.)
I use many 3 phase electric heaters below 10 KW. Immersion heater in industrial applications.
Many heater applications have to be treated as a continuous load. Can't really tell what this application is.
Immersion heaters, by the way, generally have to be counted as a continuous load whether that is really the case or not. 427.4