also a wiring diagram label on the cover of the unit says to use 1/0 and a #6 egc. Do I have to size it at 1/0 because of the label?...
Me too 110.3(B)I think so.
It has 3 lugs for field wiring and it splits off 4 conductors from those into internals.
That is a problem with many panel boards butt usually 125 amp is the largest size breaker that can be installed on the buss. It should be labeled on the panel.It actually says " 0 " so I assume that's 1/0, and it says "1" for lower currents and voltages. The other problem I have is that it's fed from a CH panel and I think 100A is the largest 3 pole CB available... None of this was in the plan so it's all extra anyway.
Storage type 422.13 makes it "continuous", 100 amp x 125% = 125, so, as jumper says 125 and #1 should be sufficient. Your 422.11(E) would limit it not to exceed 150, but keep 422.11(F) in mind also so you can subdivide the circuits if the manufacturer has not.