Re: Water Heater - Continuous Load???
422.13 is a minimum breaker size of 125%. 422.11(E) is a maximum of 150% with round up permitted. I don't see a conflict, just a bounding of breaker sizes between 125% and 150% of the heater rating, and round up to a standard breaker size is permitted.
422.13 is a minimum breaker size of 125%. 422.11(E) is a maximum of 150% with round up permitted. I don't see a conflict, just a bounding of breaker sizes between 125% and 150% of the heater rating, and round up to a standard breaker size is permitted.