gent

Member
I am told that an electric water heater must have a disconnecting means within sight, be it cord and plug, breaker, switch, whatever.
Where is this in the Code??
 

bphgravity

Senior Member
Location
Florida
Re: Water Heater Disconnect

Breakers, switches, and disconnects yes, cord-and-plug no. I do not think a water heater meets the requirements of 422.16. Water heaters should be "hard wired". :)
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: Water Heater Disconnect

This came up on a previous post. It wasn't ever 100% determined if a water heater could be cord and plug connected, however, after looking at the UL listing information, I feel it is dependant on what the manufacture states in the instructions.

The disconnecting means does not have to be within site if it is capable of being locked open.
 

noxx

Senior Member
Re: Water Heater Disconnect

I've always been taught that a water heater should have a disconnecting means, either cord or switch within reach of the unit. However, after reading more carefully the cited articles, I'm going to have to agree with Bryan regarding 422.16. Water heaters are not frequently interchanged, and their other mechanical connections are not designed to permit ready removal.

I'm still all for the local switch however, even though 422.31B allows the overcurrent device to serve that function, it seems good sense to me to have a local means.

Tom, I don't think the manufacturers' instructions would be enough by itself due to the wording of 422.16a2 which reads in part "..specifically designed to permit ready removal for maintenance or repair and the appliance is intended or identified for flexible cord connection." The "and" in there indicates, to me, that being listed or intended for a cord is not enough alone, that the appliance must also satisfy the previous requirements.

Of course, water heaters in tract homes are cord connected left and right, so it's obviously not something everyone agrees on. Interesting stuff tho.

-Noxx
 

bennie

Esteemed Member
Re: Water Heater Disconnect

In the interest of safety, all appliances including the water heater, should be cord and plug connected.
 

noxx

Senior Member
Re: Water Heater Disconnect

I don't see a safety issue with a hardwired connection, especially given that the water heater is strapped into place securely. Could you elaborate please?

-Noxx
 

physis

Senior Member
Re: Water Heater Disconnect

I find in "The Illustrated Guide to the National Electrical Code" This:

"Water heaters shall not be connected with flexible cords >>422.16(A)<<

If my interpretation is correct a water heater doesn't meet either of the two conditions required to be allowed attachment with a flexible cord.

[ May 09, 2003, 05:49 PM: Message edited by: physis ]
 

bennie

Esteemed Member
Re: Water Heater Disconnect

I think 422.16(A)(2), would work for validation of flexible cords.
 

physis

Senior Member
Re: Water Heater Disconnect

Bennie,

The case you make "for" it is probaly equal to the case that can be made "against" it. however, I never heard of a water heater being removed, repaired and reinstalled.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Water Heater Disconnect

2002 NEC
422.16 Flexible Cords.
(A) General. Flexible cord shall be permitted (1) for the connection of appliances to facilitate their frequent interchange or to prevent the transmission of noise or vibration or (2) to facilitate the removal or disconnection of appliances that are fastened in place, where the fastening means and mechanical connections are specifically designed to permit ready removal for maintenance or repair and the appliance is intended or identified for flexible cord connection.
And the commentary for this article from the 2002 NEC Handbook.

It should be understood that a cord-connected appliance is required to be specifically designed, mechanically and electrically, to be readily removable for maintenance and repair.
I do not see any reason to use cord for a water heater and as someonelse pointed out probably more money for 30 amp cord cap and outlet than a disconnect.

[ May 09, 2003, 06:11 PM: Message edited by: iwire ]
 

physis

Senior Member
Re: Water Heater Disconnect

I was going to say what Bob said but got there first.

[ May 09, 2003, 06:20 PM: Message edited by: physis ]
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Water Heater Disconnect

Yes Bennie I would agree 100% as any of those I have seen come with a factory installed cord and cord cap.
 

physis

Senior Member
Re: Water Heater Disconnect

OK Bennie, :)

[ May 09, 2003, 07:25 PM: Message edited by: physis ]
 

bennie

Esteemed Member
Re: Water Heater Disconnect

I don't really think I would connect a water heater with a dryer cord, but I don't think there is any problem with the procedure.

My dryer has been in the same place, except for moving to clean under it, for 14 years. My water heater has been changed two times.
 

bphgravity

Senior Member
Location
Florida
Re: Water Heater Disconnect

I do not know what can make two applainces have two different classifications, but for whatever reason:

Ranges, refrigerators, counter-top appliances, dish washers, disposals, dryers, washers. These can be cord-and-plug connected.

Water heaters, air-handlers, furnaces, a/c units, range hoods. These should be hard wired with means of disconnect.

The only discernible difference is the appliance installation itself. Fastened in place or not. It just seems weird to me to have a cord-and-plug attachment to a water heater. I still feel the code prohibits this, but I really cannot see any safety issue with it. :confused:
 
Re: Water Heater Disconnect

but here one catch i see few gaz fired waterheater have cord attchment there allready for blower and ingiter assambly unit and i left there with reguair singleplex outlet for it . for bigger devices if i recall the nec 422.14.a (96 code) shall be rated for 15 or 20 or 30 amps but there is a fine line for usage i am not done digging up on 02 codes yet i know there are some change there but validly i remeber that if under 1.5 kw or less can be cord attached if over 1.5 have to be hard wired i cant remeber where excat location it state there .

bob i see few peoples use 3 wire dryer cords attached to waterheater but not straght 6-30 set up at all ( straght 240 volts cord ) even thru one person did use that for both waterheater and dryer and they told me that they switch back and froth i say i am not crazy with it. it must be on seprarte crk .