I've always been taught that a water heater should have a disconnecting means, either cord or switch within reach of the unit. However, after reading more carefully the cited articles, I'm going to have to agree with Bryan regarding 422.16. Water heaters are not frequently interchanged, and their other mechanical connections are not designed to permit ready removal.
I'm still all for the local switch however, even though 422.31B allows the overcurrent device to serve that function, it seems good sense to me to have a local means.
Tom, I don't think the manufacturers' instructions would be enough by itself due to the wording of 422.16a2 which reads in part "..specifically designed to permit ready removal for maintenance or repair and the appliance is intended or identified for flexible cord connection." The "and" in there indicates, to me, that being listed or intended for a cord is not enough alone, that the appliance must also satisfy the previous requirements.
Of course, water heaters in tract homes are cord connected left and right, so it's obviously not something everyone agrees on. Interesting stuff tho.