What size OCP are the rest of you putting on a water heater in a dewelling that has a total connected load of 3500w @ 208?
what size ocp are the rest of you putting on a water heater in a dewelling that has a total connected load of 3500w @ 208?
What size OCP are the rest of you putting on a water heater in a dewelling that has a total connected load of 3500w @ 208?
What size OCP are the rest of you putting on a water heater in a dewelling that has a total connected load of 3500w @ 208?
What type of dwelling do you have that has 208v. Are these 3 phase services
You dont have 208v at your house?![]()
What type of dwelling do you have that has 208v. Are these 3 phase services. 3500 watt elements is definitely unusual around here.
What type of dwelling do you have that has 208v. Are these 3 phase services. 3500 watt elements is definitely unusual around here.
It's a 30 story condo building. Made the first final inspection on one of the units and and he had the water heater on a 30a 2-pole and he was quite upset when I told him that he needed a 25a. Now the contractor is having trouble finding 440 25a 2-pole breakers.
30 story building. The element is 3500w or 3380w I've alot of both lately. Both need 25a on them at 208v.
I bet someone is doing a lot of cussing. Are your ears ringing?![]()
Now the contractor is having trouble finding 440 25a 2-pole breakers.
30 story building. The element is 3500w or 3380w I've alot of both lately. Both need 25a on them at 208v.
So did I win something?
A 25 pound turkey with all the sides ......... including pie.![]()
Man, I already have one.
Happy Holidays to all.
It's a 30 story condo building. Made the first final inspection on one of the units and and he had the water heater on a 30a 2-pole and he was quite upset when I told him that he needed a 25a. Now the contractor is having trouble finding 440 25a 2-pole breakers.