The load is a 24KW 208 water heater.
Amp 66.6 X 125%=83.25 min. wire size.
66.6 X 150%=99.9 max. breaker size.
Exception to rule can go to next standard
size breaker. Contractor installed 100 amp
breaker #2 aluminum with 100 amp disconnect
next to water heater.
Another inspector will not pass this job,
he wants it on 90 amp breaker.
I feel that the contractor has met the code,NEC.
[ February 21, 2005, 12:20 AM: Message edited by: stevearne ]