Installation of a counter top water/ice machine. Nameplate says min ckt ampacity 19.3 amps, max OCPD 25 amps. There is a J-box on the back of it for the attachment of a cord or other wiring method. Since it needs water it is located with-in 6 feet of a sink. There is already a 20 amp GFCI receptacle in place fed by a dedicated 20 amp breaker.
Is it legal to put 12/3 cord with a 20 amp plug on this machine and plug it into the GFCI receptacle?
Also, is a typical GFCI receptacle considred a single receptacle or is a duplex?
Is it legal to put 12/3 cord with a 20 amp plug on this machine and plug it into the GFCI receptacle?
Also, is a typical GFCI receptacle considred a single receptacle or is a duplex?