What is the purpose of water pipe bonding?
If it is to meet the requirements of either 250.4(A)(3) or (4), then why must the bonding jumper be sized per 250.66 and run to the service equipment and/or grounding electrode system.
Other piping systems do not have this stringent of a requirement. Based on the wording, a 200A home could have only 2 ground rods connected by #6 as the grounding electrode system and then have a #4 water bond? Doesn't make much sense to me.
If it is to meet the requirements of either 250.4(A)(3) or (4), then why must the bonding jumper be sized per 250.66 and run to the service equipment and/or grounding electrode system.
Other piping systems do not have this stringent of a requirement. Based on the wording, a 200A home could have only 2 ground rods connected by #6 as the grounding electrode system and then have a #4 water bond? Doesn't make much sense to me.