ptonsparky
Tom
- EC - retired
You have a small three phase pump motor. 208.
Service is 240v with Hi leg. (We don't care it has one. Your motor does not care)
What is the total distance to where your pump will be? VD can be your friend in this case. Two hundred feet of 14 cu @ 5.9 Amps will give you approx 223 volts at your motor. Within limits.
To confuse things a bit. Get a VFD that allows single phase input and gives you three out. Set the parameters to match that of the motor. I would use the two legs with 120v to ground because the VFD does care about the Hi Leg.