Weather-Resistant Receptacles

Status
Not open for further replies.

NTesla76

Senior Member
Location
IA
Occupation
Electrics
Was it ever a code requirement to have outdoor receptacles marked with "WR"? If so, when did it change? I can only see the listing of the receptacle must have it labeled "WR", and not an NEC requirement.
 

NTesla76

Senior Member
Location
IA
Occupation
Electrics
Thanks for the replies. Interesting that 406.9(A) Damp Locations says the receptacles shall be a listed weather-resistant type. 406.9(B)(1) Wet Locations says receptacles shall be listed and so identified as the weather-resistant type. In my opinion, that says two different things between damp and wet locations.
 