petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
There is wordage stating raceways shall be arranged to drain. I am not aware of anything telling to drill holes in bottom of enclosures, though that is an effective way of preventing accumulation of condensation.

As I have mentioned there are enclosures that come with instructions to drill holes or remove already installed plugs/screws/etc to essentially convert the enclosure to type NEMA 3R, but those still are tighter sealed than the average 3R loadcenter cabinet or similar enclosures.
314.15 Damp or Wet Locations. In damp or wet locations,
boxes, conduit bodies, outlet box hoods, and fittings shall be
placed or equipped so as to prevent moisture from entering or
accumulating within the box, conduit body, or fitting. Boxes,
conduit bodies, outlet box hoods, and fittings installed in wet
locations shall be listed for use in wet locations. Approved
drainage openings not smaller than 3 mm (1∕8 in.) and not
larger than 6 mm (1∕4 in.) in diameter shall be permitted to be
installed in the field in boxes
or conduit bodies listed for use in
damp or wet locations. For installation of listed drain fittings,
larger openings are permitted to be installed in the field in
accordance with manufacturer’s instructions.
 