weathertight bulkhead options with LFMC fitting on one side, EMT (or multi-conductor cable) on the other side?

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Questions for the OP:

If the inside was no object, what fitting or other part would ideally be on the outside?

And:

If the outside was no object, what fitting or other part would ideally be on the inside?

Must either one or both either have or not have a removable cover? Are splices required?

I'm trying to envision what is the problem with simply sandwiching the container between the two.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
It doesn't need to be. It's just a threaded non-electrical sleeve welded in place. Sleeves are not under the purview of the NEC and can be made with any material.
You said screw conduit running thread through the plumbers coupling...that would a conduit with straight threads. My question is what fitting with female threads is suitable for connecting to straight threaded conduit?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You said screw conduit running thread through the plumbers coupling...that would a conduit with straight threads. My question is what fitting with female threads is suitable for connecting to straight threaded conduit?
A running thread should work even with a tapered coupling unless the thread patterns on each side of the coupling didn't match, then some type of straight thread coupling would be required. I know I initially said plumbing coupling which most would assume to be a tapered thread. I should have said any straight thread coupling besides an electrical one.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
they're not a listed component tho. these systems will be shipping many places/countries so we need to avoid anything they can nitpick at during installs
Why would they need to be listed? You're using them to penetrate a structure; at the penetration you could use almost anything. And good luck finding electrical fittings that will be accepted as listed in every single country. It's hard enough finding fittings listed for the US and EU, let alone everywhere else.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
A running thread should work even with a tapered coupling unless the thread patterns on each side of the coupling didn't match, then some type of straight thread coupling would be required. I know I initially said plumbing coupling which most would assume to be a tapered thread. I should have said any straight thread coupling besides an electrical one.
As far as I know there are no electrical fittings that have female threads that have been evaluated for use with straight male threads.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
As far as I know there are no electrical fittings that have female threads that have been evaluated for use with straight male threads.
I'm thinking of any non electric straight threaded coupling which would merely be a sleeve for a RMC running thread. The coupling (sleeve) would have no affect or bearing on the electrical installation so it could be welded, epoxied, glued, etc in place.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
As to the OP, apparently there's something called a uniseal fitting, which is a sort of sealing rubber grommet. So you can drill a specified size hole through the metal container, install the uniseal fitting, and then just push through any cylindrical penetration of the matching OD. Not sure if they are made in EMT sizes, but they are made in Schedule 40 sizes.

Cheers, Wayne
 

letgomywago

Senior Member
Location
Washington state and Oregon coast
Occupation
residential electrician
As far as I know there are no electrical fittings that have female threads that have been evaluated for use with straight male threads.
South wire SimPush rigid fittings are and they are Rain tight as well.
 

Attachments

  • Screenshot_20241120_145747_Firefox.jpg
    Screenshot_20241120_145747_Firefox.jpg
    391.2 KB · Views: 5
  • Screenshot_20241120_145757_Firefox.jpg
    Screenshot_20241120_145757_Firefox.jpg
    572.6 KB · Views: 5

letgomywago

Senior Member
Location
Washington state and Oregon coast
Occupation
residential electrician
have never seen that, but I would never even think of permitting a push on conduit connection one of my jobs
They're listed they exist are listed for equipment grounding and that's what the reply was for since the bickering back and forth about a silly bulkhead.

I agree that welding couplings isn't allowed but I can also see someone making a listed coupling that doubles as support. It would need to be in the manufactures instructions.

In the end there's better ways to do this whole install without misusing materials.
Use a fromtoo emt to rigid nipple in the bulkhead and a rigid ripple from bulkhead with from too for rmc to flex.

I think people are picking some stupid anthills to stand on in this discussion too BTW.
 
I think Don's question is how do you make a raceway connection to each end of your RMC running thread, if the whole thing is straight threaded?

Cheers, Wayne
As far as I know there are no electrical fittings that have female threads that have been evaluated for use with straight male threads.
Ok so say you have Rob's running thread idea. I see several options from there:

1. But a box on the inside and the outside with locknuts. What could be wrong with that?

2. What about a RGS coupling and a 90 degree flex/sealtight connector on that? IS that one of those silly academic things where we cant thread a connector into a coupling? I just did that today LOL.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
My first two posts were ignored, so I'll try one more time.

Why is this not as simple as, say, a pair of LBs with a close nipple between them, sandwiching the container wall and an O-ring or two?
 