So, it has been a while since I was able to return to this job. The installers forgot to measure the door opening to the enclosed porch and the tub didn't fit. Had to wait on a new tub that did fit.
Using this GFCI disconnect:
https://www.lowes.com/pd/Eaton-50-Amp-Metallic-Spa/50416388
I verified all of my wiring was correct. When I tested with my digital multi meter, it did not trip. Again I used my old solenoid tester and it tripped
the GFCI switch (which actually looks like a circuit breaker).
Testing with solenoid tester at the actual GFCI switch: Test any hot to neutral - no trip. Test Hot to Hot - no trip.
Testing with solenoid tester at the other end of 25 feet of sealtite and #6 AWG: Test any hot to neutral - no trip. Test Hot to Hot - TRIP.
Testing with Digital Multi meter at the actual GFCI switch: Test any hot to neutral - no trip. Test Hot to Hot - no trip.
Testing with Digital Multi meter at the other end of 25 feet of sealtite and #6 AWG: Test any hot to neutral - no trip. Test Hot to Hot - no trip.
I connected the hot tub to my wiring and it seems to be working fine now.
I'm not sure what was going on.