Hello, I’m an electrician, and this issue has been perplexing me.
So I went to this old lady’s house and she has one of those old pushmatic panels. I tested voltage at the panel at the main lugs and I got 240v between phases and 120v between each hot and neutral with all of the breakers turned off.
As soon as turn on one of the breakers I’ll get 220v between one of the hots and neutral, and if my memory serves me correctly like 20ish v on the other hot to neutral, still getting 240ish v between phases.
When I turned that breaker off, I started turning breakers on, one by one and I was getting normal voltages (240 between phases, 120v between each hot and neutral), until I turned on like 3 breakers (each were 1p, 15a) that each distorted the voltage readings until I was getting 115v one hot to neutral and like 124v (again if my memory serves me correctly) on the other hot to neutral still getting 240ish v between hots.
I know it’s probably a loose neutral (I suspect at the meter), and my question pertains to pinpointing it and the why part. How is it possible to have normal voltages between phases and then when I turn on a breaker it makes all my voltages wonky at the panel? The breaker I turned on that gave me the 220v from 1 leg to neutral and 20v the other leg to neutral at the panel was feeding kitchen and bathroom outlets. I would think if there was a loose neutral in the outlet itself that it would show at the outlet but not mess with the hot to neutral voltages at the panel. And then the other 1p - 15a breakers that progressively showed messed up readings at the panel (with the kitchen circuit turned off) perplex me as to how that’s happening.
Any help in better in pin pointing, diagnosing and troubleshooting is much appreciated.
Thanks in advance.
So I went to this old lady’s house and she has one of those old pushmatic panels. I tested voltage at the panel at the main lugs and I got 240v between phases and 120v between each hot and neutral with all of the breakers turned off.
As soon as turn on one of the breakers I’ll get 220v between one of the hots and neutral, and if my memory serves me correctly like 20ish v on the other hot to neutral, still getting 240ish v between phases.
When I turned that breaker off, I started turning breakers on, one by one and I was getting normal voltages (240 between phases, 120v between each hot and neutral), until I turned on like 3 breakers (each were 1p, 15a) that each distorted the voltage readings until I was getting 115v one hot to neutral and like 124v (again if my memory serves me correctly) on the other hot to neutral still getting 240ish v between hots.
I know it’s probably a loose neutral (I suspect at the meter), and my question pertains to pinpointing it and the why part. How is it possible to have normal voltages between phases and then when I turn on a breaker it makes all my voltages wonky at the panel? The breaker I turned on that gave me the 220v from 1 leg to neutral and 20v the other leg to neutral at the panel was feeding kitchen and bathroom outlets. I would think if there was a loose neutral in the outlet itself that it would show at the outlet but not mess with the hot to neutral voltages at the panel. And then the other 1p - 15a breakers that progressively showed messed up readings at the panel (with the kitchen circuit turned off) perplex me as to how that’s happening.
Any help in better in pin pointing, diagnosing and troubleshooting is much appreciated.
Thanks in advance.