Welder spec. requires 50A outlet, 208/3 for connection, but 100A/3P, 208/3 breaker in panel dues to inrush. Welder's full load amp. is around 38A, the inrush current is 78A. However, 100A wires is too large to terminated at 50A outlet, EC suggests to install a disconnect before the outlet to reduce wire size and be able to connect to the 50A outlet. Should the disconnect be fused as fault current at the outlet is more than 10KA? If so, should fuse size match breaker size, i.e. 100A or can be smaller, or = 38A x 1.75 = 66.5A, next standard fuse size is 70A per NEC 430.52?