i am an Electrician that runs a service truck
I have a 115v 20a 2.5Kw welder w/20% duty cycle
that iam trying to install a circuit for and 630 is confusing to me
![]()
Did this unit come with a NEMA plug installed on it?
Perhaps a 5-20P?
If so I would forget all about Article 630 and just install a 20 amp 125 volt circuit for it. The only reason I know of to use Article 630 is to save money. The use of Article 630 allows smaller conductors to be used and this can be significant if you have a number of large welders, you have one small welder and there is no reason not to run a full size circuit to it.
I feelt the same way until the customer says he's tripping the circuit.
He's on a 20a circuit now.
630 says multiply the current by .45
and fuse it at no more than 300% ?
does that mean #10 wire and 60a breaker?
I have a 115v 20a 2.5Kw welder w/20% duty cycle
I feelt the same way until the customer says he's tripping the circuit.