I think the more general point is that lightning currents are not comparable to welding currents in either behavior or duration. It does not follow that the welding currents are safe because lightning currents may, in the odd circumstance, travel over the same metal without causing damage. And of course, sometimes lightning on EGCs does cause damage.
that wasnt the point, and i dont think anyone was stating such.
the point was, LPS is to be tied to GEC. ok, which also means its tied to EGC. ok, and some say it doesnt matter that its tied to EGC because like dumping a buck of water in sink it all goes down the drain, except one minor fact, GEC also has ohms, which means a % of the LPS amps also runs over EGC to wherever, hence why i said LPS systems should really be isolated from the wiring of a structure. but, isolation is not ez w/ lightning.
i think iron structures, the iron is the GEC and not EGC, so they can clamp a beam near the welder and then run out 100ft (or whatever) to stick weld, etc.
as for welding amps on EGC (one leg of the welder), that can be an issue depending on how the EGC stuff is deployed/connected. however, a burn hole in MC might be amps taking a new route, and it created a haz point on the MC and it eventually melts, which can obviously cause an issue for the wires inside.