Seven-Delta-FortyOne
Goin’ Down In Flames........
- Location
- Humboldt
- Occupation
- EC and GC
Scenario: 1 phase 230V well pump, separate pressure pump in system, so well pump only pumps to storage tanks.
HO called me because they feel the well pump hasn’t been coming on much. It is very typical for this well to run dry anywhere from mid summer to late fall.
System is as follows: 20A 2P breaker - low water/overload control box - box with contactor for float switch - motor starter with start capacitor.
As far as my opinion, it’s working as it should. Controller is showing OL when float switch calls for water.
What I did: Jumpered float switch; controller shows OL.
Bypassed low water shut down, jumpered float switch, nothing comes out of pump, but clamp meter shows 31-32 amps going to well pump, load side of motor start controller.
Tested capacitor, tested good.
Pulled motor leads from controller. Tested Ohms. Got 15-16 ohms on run windings. Manual says 3.5-5.6.
Meggered motor leads. Got 220M ohms on both leads.
Two areas of concern for me: In the interest of being thorough, I don’t have any way to absolutely verify that the pump is going into OL because of no water, or because of a possible problem with the impeller, clogged screens, etc., without pulling the pump. Unless there is something else I can do.
And 2, what would be the cause of having a slightly higher Ohm reading? I know what an infinity would mean, but what about when it’s just a little higher than it should be?
Pump was replaced about 6 years ago, so shouldn’t be worn out ideally.
HO called me because they feel the well pump hasn’t been coming on much. It is very typical for this well to run dry anywhere from mid summer to late fall.
System is as follows: 20A 2P breaker - low water/overload control box - box with contactor for float switch - motor starter with start capacitor.
As far as my opinion, it’s working as it should. Controller is showing OL when float switch calls for water.
What I did: Jumpered float switch; controller shows OL.
Bypassed low water shut down, jumpered float switch, nothing comes out of pump, but clamp meter shows 31-32 amps going to well pump, load side of motor start controller.
Tested capacitor, tested good.
Pulled motor leads from controller. Tested Ohms. Got 15-16 ohms on run windings. Manual says 3.5-5.6.
Meggered motor leads. Got 220M ohms on both leads.
Two areas of concern for me: In the interest of being thorough, I don’t have any way to absolutely verify that the pump is going into OL because of no water, or because of a possible problem with the impeller, clogged screens, etc., without pulling the pump. Unless there is something else I can do.
And 2, what would be the cause of having a slightly higher Ohm reading? I know what an infinity would mean, but what about when it’s just a little higher than it should be?
Pump was replaced about 6 years ago, so shouldn’t be worn out ideally.