Yeah, no pigtail on this one.
With a new controller it does the exact same thing, so it can’t be a bad relay.
It’s not common for these pumps to fail, especially after such a short time, but, if you have eliminated all other possibilities, then whatever remains, however extraordinary, must be the truth.
I have bypassed the OL and got LRA on the pump. I have tested and then switched out the start cap and relay. I have bypassed the float switch. I have ohm’d out, and meggered the pump windings, and the readings are perfectly within manufacturer specs.
Whatever the problem is, bad splice, jammed impeller, corroded shaft, whatever, must be at the bottom of the well, because I’ve tested everything (that I can think of) at the top.
I know your specialty is well pumps, so if you have any other advice I would certainly be receptive.