Additional, I know you are not the plumber here but this is a trick I use for low performing wells to help protect it. I install a gate valve right off the pitless as a throttling valve and and tune that while I monitor the dynamic draw down on the well to ensure there is decent balance there. I had a case about a year ago on a special drip irrigation system but the well (I even confirmed in tests) was only safe at 2GPM. I throttled a personally selected low lift 1/2HP pump just below that and tuned the irrigation drip to run with that, and I ran a very large volume tank with prescribed watering intervals so we would get good recharge.Yeah, no pigtail on this one.
With a new controller it does the exact same thing, so it can’t be a bad relay.
It’s not common for these pumps to fail, especially after such a short time, but, if you have eliminated all other possibilities, then whatever remains, however extraordinary, must be the truth.
I have bypassed the OL and got LRA on the pump. I have tested and then switched out the start cap and relay. I have bypassed the float switch. I have ohm’d out, and meggered the pump windings, and the readings are perfectly within manufacturer specs.
Whatever the problem is, bad splice, jammed impeller, corroded shaft, whatever, must be at the bottom of the well, because I’ve tested everything (that I can think of) at the top.
I know your specialty is well pumps, so if you have any other advice I would certainly be receptive.
In those gate valve cases, I remove the handle and ziptie it and a tag to the pipe so people don't jack with it.