I install Weather Equipment, often in the middle of nowhere out here in the West.
Usually at our Weather sites, the Service Feed comes from a small 208/ 120V 100A transformer the local Utility has installed on a Pad along with a Meter and we take it from there at the Meter Base.
Usually we put in a 100A Fused Disconnect Switch, a 100 A NEMA 4R Panel with 20 circuit breakers and a TVSS and feed 5 to7 Weather sensors (Wind, Visibility, Cloud, Freezing Rain,….) from that .Its all in accordance with the NEC Code
I’m now at a site where all we have is One Wind Sensor and a LED navigation Light.
The Service is actually one 20A breaker on a 100A panel 600 feet away at a small school building. The conductors run through an old underground conduit and are 8AWG.
The conduit is pretty long and old. I don’t think I have the tools to pull new conductors. Even if I pulled new ones, it wouldn’t do much good since I only have one 20A breaker upstream.
At the site, I would put in a a 40A DoubleTapped Disconnect Switch fused at 20A, since we have 8AWG conductors and a TVSS, but what do I do for a Panel?
I can’t find one that small meets our standards
Can I substitute two individual 20A molded case Circuit breakers and not use a Panel and still meet NEC Code? (The load on each of the breakers is only 5 or 6A, but we can’t use breakers that small.)
Each of the 2 Individual Molded Case breakers would come from the 40A Double tapped disconnect
That meets requirements We just need to feed the Wind Sensor electronics and a LED Light.
I’m worried that somehow I might not meet the NEC Code. because I’m using two individual molded case breakers instead of a Panel.
Is my proposal okay?
Usually at our Weather sites, the Service Feed comes from a small 208/ 120V 100A transformer the local Utility has installed on a Pad along with a Meter and we take it from there at the Meter Base.
Usually we put in a 100A Fused Disconnect Switch, a 100 A NEMA 4R Panel with 20 circuit breakers and a TVSS and feed 5 to7 Weather sensors (Wind, Visibility, Cloud, Freezing Rain,….) from that .Its all in accordance with the NEC Code
I’m now at a site where all we have is One Wind Sensor and a LED navigation Light.
The Service is actually one 20A breaker on a 100A panel 600 feet away at a small school building. The conductors run through an old underground conduit and are 8AWG.
The conduit is pretty long and old. I don’t think I have the tools to pull new conductors. Even if I pulled new ones, it wouldn’t do much good since I only have one 20A breaker upstream.
At the site, I would put in a a 40A DoubleTapped Disconnect Switch fused at 20A, since we have 8AWG conductors and a TVSS, but what do I do for a Panel?
I can’t find one that small meets our standards
Can I substitute two individual 20A molded case Circuit breakers and not use a Panel and still meet NEC Code? (The load on each of the breakers is only 5 or 6A, but we can’t use breakers that small.)
Each of the 2 Individual Molded Case breakers would come from the 40A Double tapped disconnect
That meets requirements We just need to feed the Wind Sensor electronics and a LED Light.
I’m worried that somehow I might not meet the NEC Code. because I’m using two individual molded case breakers instead of a Panel.
Is my proposal okay?