Do wet bar counter tops need to be laid out like a kitchen counter top (210.52 c 1)? I getting two different inspectors opinions.
That was added in 2008, and kept in 2011. The 2005 just said "kitchens." So it matters which code cycle applies to the installation. It also matters how this alleged "countertop" is constructed. Does it sit up against a wall, or does it look more like a peninsula or an island. Finally, it could be argued that this horizontal surface is not a "countertop," a word that is not defined in the NEC. I can envision a flat surface with legs (almost like a table), with a sink at one end, and with space under the flat surface for the legs of a person sitting on a stool. That is not a "countertop."210.52 (C) is for countertops, notes the rooms and then says "similar areas."
Kitchen.
An area with a sink and
permanent provisions for
food preparation and cooking.
To stir things a little more -
If a wet bar is a "similar area" and needs to follow kitchen requirements then many patios should need to follow kitchen requirements also.
Arc fault protection is also required for the outlets if the wet bar is located in any room listed in 210.12(B).IMHO, the only requirement you should be concerned about is the GFCI receptacle within 6' of the sink at the wet bar.
This is the most correct statement because they will have final say if it passes or not.Probably the best solution is to get your opposing AHJ's together and have a discussion.
This is the most correct statement because they will have final say if it passes or not.
Arc fault protection is also required for the outlets if the wet bar is located in any room listed in 210.12(B).
I never said they would be right I was saying that sometimes it is better not to fight city hall but work with them.Well, just because they all agree, doesn't mean they're not wrong.:roll:
Did I just say that out loud?