Cant find much about countertop space for bars,wet bars,ect...
Gfi. 2 ft rule still applies?
Gfi. 2 ft rule still applies?
allenwayne said:You mean gfci 6 ft rule don`t you??? A wet bar isn`t restricted like a kitchen countertop is 1 ft,2 ft, 4 ft.
Don(C) Countertops In kitchens and dining rooms of dwelling units, receptacle outlets for counter spaces shall be installed in accordance with 210.52(C)(1) through (C)(5).
don_resqcapt19 said:Mike,
Steve is correct...if it is a countertop in the kitchen or dining room the kitchen spacing rules apply.
Don
jcole said:JW
Where in the code does it say that receptacles within 6 ft of a sink have to be gfci protected? I have always heard this and complied but never have found in code.
charlie b said:Three points to keep in mind.
1. 210.8(A)(7) only applies to dwelling units. There is no ?six foot rule? anywhere else.
2. 210.8(A)(7) only calls out three types of sinks. Sinks in bathrooms and kitchens are covered by separate sub-parts of 210.8(A). So if you can come up with a sink that is not in the kitchen or a bathroom, and is neither a laundry sink nor a utility sink nor a wet bar sink, then you don?t have to protect receptacles with six feet with GFCIs.
3. Some jurisdictions, and Washington State is one, have adopted a broad definition of ?kitchen.? So you might have to apply the kitchen countertop rules to a wet bar or other areas of a dwelling unit, if ?food preparation? takes place in that area.
The broadness doesn't go quite that far, at least not here in WA. Where you eat the food is not relevant. All that matters is where you prepare it.steve66 said:On point 3, don't forget kitchen countertop rules also apply to countertops in dining rooms. So if they use a broad definition for a kitchen, then a dining room could be almost anywhere you might eat food.