Wet Location Conductors

Status
Not open for further replies.

jflynn

Senior Member
Does anyone see a problem using type THWN-2 insulation in a wet location?The reason I ask is we had trouble finding the wire size we needed in XHHW and looking @ article 310.8 (c) type THWN-2 is listed for wet locations.We found the size we needed with THWN-2 insulation and it is more cost effective.
 
jflynn said:
Does anyone see a problem using type THWN-2 insulation in a wet location?

type THWN-2 is listed for wet locations.

You've answered your own question.:smile:

steve
 
While they are both suitable conductors per the code, XHHW is often specified for underground and other harsh conditions. It is a tougher insulation and will last longer.
 
While the code permits both in wet locations THWN-2 is rated for 90 degree C while XHHW is only rated for 75 degrees C in wet locations. If derating is involved that could be a factor is choosing one over the other.
 
On this subject, but off on a slight tangent, how does one evaluate components to determine if they are intended for wet (in my case, outside roof top) locations.

Cases in point: Fluorescent fixture behind a fabric canopy sign - totally exposed at the top to the elements (1st photo below).

Cable directly on the roof (nice use of a paint can for ballast, eh?).

http://i15.photobucket.com/albums/a352/TonyPE/IMGP0242_edited-1.jpg
http://i15.photobucket.com/albums/a352/TonyPE/IMGP0241_edited-1.jpg
 
If it is in a wet location it must be listed for wet locations.

If it is in a damp location it must be listed for damp or wet locations.
 
Just by looking at the pictures I can tell you that the junction boxes and EMT fitttings are not rated for wet location.

As far as the conductors, you could open a JB and see what type conductors were used.

All in all a pretty crappy installation, and definitely not code compliant.

Just my opinion
steve
 
iwire said:
If it is in a wet location it must be listed for wet locations.

If it is in a damp location it must be listed for damp or wet locations.

Is there any way to make this determination on items in service for maybe 20 years or more?
 
tonype said:
Is there any way to make this determination on items in service for maybe 20 years or more?

You need to look in Article 100 for the definitions of location, wet and location, damp.
 
infinity said:
While the code permits both in wet locations THWN-2 is rated for 90 degree C while XHHW is only rated for 75 degrees C in wet locations. If derating is involved that could be a factor is choosing one over the other.



Good point,do you know if AL. wire is made with THWN-2?We seem to only be able to find it in XHHW.We had the exact issue you mention about derating with XHHW...
 
jflynn said:
Good point,do you know if AL. wire is made with THWN-2?We seem to only be able to find it in XHHW.We had the exact issue you mention about derating with XHHW...

If you can use XHHW-2 it rated for 90 degrees C in wet locations.
 