goldstar
Senior Member
- Location
- New Jersey
- Occupation
- Electrical Contractor
I know the NEC states that RX cable cannot be used inside PVC when installed outdoors. I'd just like to know the CMP's thinking in making this determination in some instances. Let's say you have an 40 amp AC disconnect located about 25' away from the breaker panel in a residence. You run 8/2 RX cable from the breaker panel, through the basement and directly into the back of the disconnect. The wiring INTO the disconnect is not considered a wet location but the wiring inside the fixture whip is. OK - no problem. Now let's say that you have to elevate the disconnect a bit to make it at a serviceable height. You install an LB stubbed into the basement and a terminal adapter and now that 8/2 RX cable is in considered to be in a wet location.
In another instance, you have to run a line for an AHU in the attic. You can't find a chase from the basement to the attic so you run the cable outside and sleeve it in a few lengths of PVC with an LB on each end stubbed into the attic and basement. The way I see it, unless you're in New Orleans during Hurricane Katrina and your house gets completely submerged, there's no way any water is getting inside that PVC. How can this be considered a wet location ?
To make matters worse, if you STUB PVC into a location (technically speaking) you need to have a cable fitting to hold the cable you've just installed. That means you'll have to install a PVC-female adapter and an RX connector to clamp onto the cable. That way the cable is properly terminated at both ends of the PVC.
I know this can all be Code compliant if you use just UF cable but IMHO it just adds more unnecessary $$ onto a job that you're trying to compete for.
BTW, we all know that the conductors inside RX cable are THHN but manufacturers don't mark the individual conductors. The wire rating is on the outer jacket. I think this is a scam perpetrated by wire manufacturers to get you to buy and stock more wire.
Sorry - just venting. An overwhelming majority of the NEC sections make sense but some don't IMHO.
In another instance, you have to run a line for an AHU in the attic. You can't find a chase from the basement to the attic so you run the cable outside and sleeve it in a few lengths of PVC with an LB on each end stubbed into the attic and basement. The way I see it, unless you're in New Orleans during Hurricane Katrina and your house gets completely submerged, there's no way any water is getting inside that PVC. How can this be considered a wet location ?
To make matters worse, if you STUB PVC into a location (technically speaking) you need to have a cable fitting to hold the cable you've just installed. That means you'll have to install a PVC-female adapter and an RX connector to clamp onto the cable. That way the cable is properly terminated at both ends of the PVC.
I know this can all be Code compliant if you use just UF cable but IMHO it just adds more unnecessary $$ onto a job that you're trying to compete for.
BTW, we all know that the conductors inside RX cable are THHN but manufacturers don't mark the individual conductors. The wire rating is on the outer jacket. I think this is a scam perpetrated by wire manufacturers to get you to buy and stock more wire.
Sorry - just venting. An overwhelming majority of the NEC sections make sense but some don't IMHO.