Jim, I think you are over reacting.
Jim W in Tampa said:Yes as per the location but that does not say you can install romex in it while wet
Location, Dry. A location not normally subject to dampness or wetness. A location classified as dry may be temporarily subject to dampness or wetness, as in the case of a building under construction.
Does that mean a 110.3(B) issue if it gets wet? However, just what constitues "excessive" is anybodys guess.paul said:Southwire's site says their product shall not be subject to excessive moisture or dampness.
Yep, and the coffee I got at Mickey D's says "Caution Coffee is Hot". Almost every product has a Captain Obvious warning label for consumer protection.paul said:Southwire's site says their product shall not be subject to excessive moisture or dampness.
Jim W in Tampa said:Southwire seems to think it matters.That paper in it was intended to be kept dry.
iwire said:But Southwire also said it's OK if the outside gets wet as long as it does not get inside. :grin:
.....For example, a building may be subject to rainfall while under construction, and water may come in contact with the outer jacket of nonmetallic-sheathed cable. This is not prohibited by the[FONT=Arial,Arial]NEC[/FONT]. The UL Standard for Safety for Nonmetallic-Sheathed Cables, ANSI/UL 719, requires Dielectric Voltage-Withstand Tests after 24-hour water immersion of cable samples (with ends in free air). If the ends of the cable are immersed for any period of time, however, the internal paper wrapping around the bare equipment grounding conductor will absorb and transfer the water into the cable assembly. The water may then start degrading the insulation or possibly corrode the conductors. If the cable comes into contact with contaminated water, the contaminants may also act on the insulation or conductors. Over time, failures can occur......