150109-1025 EST
fifty60:
Your various questions could be better understood and responded to if you provided a more complete description of your problem and limitations, and you need a more fundamental understanding of how the different components you use operate.
Your present problem appears to be:
1. You have some sort of motor with an internal relay that has a contact wetting rating of 100 mA, but no specification at what voltage. At 10,000 V I can probably breakdown any contamination layer on normal contacts.
Suppose you really need 100 mA of current at 24 V DC for reliable operation of your system, then you have to provide that as a source. Thus, you need a 24 V supply that is switched by your relay and a load resistor of 240 ohms. The next smaller nominal is 220 ohms. Power dissipation at 24 V and 220 ohms is 2.6 W. Use a 5 W resistor.
2. What are the specifications for the PLC input. We have no clue except that you mentioned 7 mA. Is it AC or DC? Not mentioned.
With the additional information you supplied it is probably a nominal 24 V DC, but possibly not and is only a TTL input with a 714 ohm pull-up resistor (highly unlikely).
Another is an optically coupled input requiring a minimum of 7 mA, but at what voltage?
Or possibly it is an optical coupler that internally has a 7 mA pullup, and when you short the PLC input terminals 7 mA flows externally.
And there are other possibilities. Provide information. Exactly what this PLC input is will determine how you interface.
Some experiments on relays I have sitting around.
A Fluke 27 in ohms position has an open circuit voltage across the terminals of about 0.75 V, and a short circuit current of about 0.46 mA.
Measuring a normally closed contact pair on a Potter & Brumfield KUP relay (20 to 30 years old) reads about 0.3 ohms on either a 5 A or 10 A relay (silver vs silver-cadmium-oxide contact material). This is essentially the reading of the two test probes shorted together. Thus, not an accurate contact resistance measurement, but it is low.
On a very old sensitive relay (10,000 ohms coil, pull-in 12.5 V, 16 mW), thus low contact pressure, the normally closed contacts read open with the Fluke 27. Probably silver contacts.
When using each of the following source voltages, and a 100k series resistor the contact voltage drop was about: .
10 V ---- 30 to 80 mV
1 V ----- 2 to 50 mV
0.1 V --- 1 to 15 mV
0.01 V -- 4 to 7 mV
You can calculate the current in each case. The environment can have a major affect on contact resistance.
.