To get rid of the several watts dissipation with a shunt resistor, then the following could be used if you really believe that current is the only criteria in determining whether or not contacts conduct.
Build your own reed relay. See http://en.wikipedia.org/wiki/Reed_switch .
A typical reed requires 10 to 60 ampere-turns to close. Get a sensitive reed, make a coil with 200 turns, use your motor contacts to switch 100 mA thru the reed relay. This will take about 250 inches of wire, 20 ft. Number 26 wire is 41 ohms per 1000 ft. Coil resistance is about 1 ohm. Power dissipation in the coil is about 10 mW. More power will be dissipated in the diodes to generate the DC for thre reed relay than in the reed relay coil. Note I have not mentioned the power lost in the transformer to get this low voltage. So instead try a switching power supply from the 24 V DC,
Note: I don't really suggest this as practical. It is simply another way to skin the cat.
.
To get rid of the several watts dissipation with a shunt resistor, then the following could be used if you really believe that current is the only criteria in determining whether or not contacts conduct.
Build your own reed relay. See http://en.wikipedia.org/wiki/Reed_switch .
A typical reed requires 10 to 60 ampere-turns to close. Get a sensitive reed, make a coil with 200 turns, use your motor contacts to switch 100 mA thru the reed relay. This will take about 250 inches of wire, 20 ft. Number 26 wire is 41 ohms per 1000 ft. Coil resistance is about 1 ohm. Power dissipation in the coil is about 10 mW. More power will be dissipated in the diodes to generate the DC for thre reed relay than in the reed relay coil. Note I have not mentioned the power lost in the transformer to get this low voltage. So instead try a switching power supply from the 24 V DC,
Note: I don't really suggest this as practical. It is simply another way to skin the cat.
.