Here's what I have.....
Underground, POCO fed meter back to back with 200A MB Panel at a town green.
Within a 3'x3' 3R enclosure, the panel has 10 20A SP breakers feeding 10 GFCI receptacles. There are no other loads.
On Wed. afternoon the town's Electrical Inspector failed my 4/0 aluminum (180A@75C?) between the meter load lugs and the 200A Breaker line lugs.
I have a calculated load of 7.5A - 220.14
SEC sized to carry load - 230.42(A)
OCPD sized per 240.4(B)
Table 310.16 and "article 230" are the best I can get out of him.
Am I overlooking something?