jumper
- 3 Hr 2 Min from Winged Horses
For the record, I have never seen/used/heard of those covers.
Of course not, you are too busy sneaking into people’s backyards and using PVC boxes to dig holes and bury GFCIs.
Wow I'm surprised at the number of people who have never seen one of these. I honestly thought outdoor panels had all those knockouts in the bottom of them so you could bring all your wires out of the outside wall of your house and into the bottom of the panel and cover them with a pop box if you wanted to. The pop box pictured in my earlier post is the most professional ones made. I've seen others that you can buy that are less than legit looking and I've seen homemade looking ones as well.....lol
The problem is that NM can't be used in damp or wet locations. Coming out of the bottom KOs like that and into the house is a violation. That cover only covers something up that can't be done in the first place.
-Hal
I have a decent head start, in CA at the moment......
Lemme go check flights at SFO. Wonder what flight time to Australia is?
Hmmm, I knows a fella down there too. Thanks fer the heads up.
...........I've said here before how I believe outdoor panels except for disconnects should be illegal, this is beyond......
The inside of a 3R enclosure is not considered 'outside'. Only the interiors of raceways are.
Yep.
Could you please explain that to ActionDave and Al in Minnesota, please.
We had a bit of a disagreement on the subject.
If you feel otherwise, feel free to submit a proposal. Forms will be in the back of your current codebook.
I will, right after I submit one eliminating AFCIs. :happyyes:
-Hal
Yep.
But if the pop cover were made of wood and covered in siding it would be perfectly acceptable, no?The problem is that NM can't be used in damp or wet locations. Coming out of the bottom KOs like that and into the house is a violation. That cover only covers something up that can't be done in the first place.
I've said here before how I believe outdoor panels except for disconnects should be illegal, this is beyond. Your inspectors aren't doing their job unless there is some TN amendment to the NEC that would allow NM in outdoor locations.
-Hal
A panel, jbox, or whatever, that is outside the building is outside. That is not hard to figure out.
Just don't walk outside after drinking it because your insides will then be outside and that could get messy.Does that make the interior of a rated enclosure a wet location?
How is the interior of said enclosure outside? Exposed to weather and such as it were?
I have a half a pot of coffee left if you want to spend time on this juxtaposition?
It hasn’t been all that long ago we could sleeve romex in an outside conduit for protection and the OPs item, whatever it is called, fills a need. It certainly looks better than some of the stuff I’ve seen ‘custom built’ for the same purpose. I wouldn’t try to get buy with it for new construction now, but sure would have in years past.
...So here's my problem. If a raceway which is sealed up pretty damn good is considered a wet location, how is it that a 3R enclosure is considered a dry location with all it's slots and openings, none of which are even gasketed. It's like Swiss cheese in a driving rain.
Either go to a NEMA 4 or, better yet put it inside. But the NEC, not being a design guide doesn't care if the breakers have to be replaced as long as their failure doesn't burn the house down.
Then again what happens if corrosion prevents them from tripping?
-Hal