How about the most common thing inspectors fail you for when you know it's right but the inspector is not to smart
Sent from my SM-G950U using Tapatalk
Agreed
从我的 iPhone 发送,使用 Tapatalk
Because they are looking at it like the PV system is feeding to the panel (like it's usually drawn). Being an electrician I always plan check it backwards from the service to the panels. I just heard someone say that an inspector made him change it the other day, in another jurisdiction of course.
We have to pay before we hear any specific answers from you?I give an 8 hour seminar on this topic.
:thumbsup:Not charging enough for your services.
Oh, I get why an inspector might look at it that way, but of course it is wrong. You'd think that all they would have to do to see it is to realize the the blades and fuses would be hot when the switch is open. I can't find anything in the NEC that explicitly says this, but it should be as obvious as not sticking your finger into a live light socket. That's not in the code, either.
One thing that should be obvious is that the OCPD in a PV inverter output circuit is to protect the conductors from fault current coming from the service; an inverter is a current limited device and if a system is designed correctly the inverter is incapable of endangering the conductors. In the event of a fault in the inverter circuit, the direction of the current flow is reversed from normal operation, going through the switch from line to load. That should make the inspector happy.
But you know all that, right?
No just have to many examples to list but here's a couple.We have to pay before we hear any specific answers from you?
:thumbsup:
I don't know of any inspector that would pass that around here without the grounds tied together either with a Buchanan, wago, or a wire nut.
you're kidding about the one wire being left long part right?
Incomplete for rough-in inspection, otherwise no problem except for the left-handed twist.
I don't think he is kidding. I think he is talking about leaving one of the EGC long to use as the pigtail to the device.
I got the impression he was saying that one wire long was a code violation of some kind. what is pictured is fine just needs a Buchanan crimp or a green wire nut with the pigtail pass through the end.