I have customer owned 13.2kv delta to 480/277V wye customer owned transformer. Primary of the transformer also belongs to customer.
The customer owned transformer one set feeds switchboard and another set of secondary conductors feed fire pump controller. The line side of the fire pump is connected to jockey pump.
In the below attached sketch conductor that connect the fire pump controller supply conductors on line side to jockey pump is circled green. The green circled conductors cant be feeder taps since their is no overcurrent protection device upstream. What are the green conductors? If they are tap conductors then I don’t see it in NEC 2017 Article 695 as call them tap conductors.

The customer owned transformer one set feeds switchboard and another set of secondary conductors feed fire pump controller. The line side of the fire pump is connected to jockey pump.
In the below attached sketch conductor that connect the fire pump controller supply conductors on line side to jockey pump is circled green. The green circled conductors cant be feeder taps since their is no overcurrent protection device upstream. What are the green conductors? If they are tap conductors then I don’t see it in NEC 2017 Article 695 as call them tap conductors.