110.9 AIC calculations are almost never provided until requested and even then halve the time you need to explain it to the designers. And everything Joe listed.
I will 2nd that!
110.9 AIC calculations are almost never provided until requested and even then halve the time you need to explain it to the designers. And everything Joe listed.
Where do you put the home runs on a circuit for multiply rooms?
Do you always put it to the closest point in respects to the panel?
Do you just run it to any light on the circuit for a clear presentation or do you bring it to the switch?
If you don't bring the power to the switch then your creating either a secondary wire or conduit back to switch or possibility creating a raceway in a light that is not rated for the service.
While it might be understood where to bring a branch circuit, some would say it is simple enough.
If the work is UL or quality inspected, its destracting to have to argue with an inspector why one did not follow the Spec's or drawing as shown.
Do you ever look at the HVAC plan and the sprinkler plan for the layouts in hallways for Grilles and head placements? Seems no one ever does.
Either one of two things happen everyones needs to be in the same space or there's no over head space to get by the HVAC main trunk in the hallway.
Then theres always seems to be some problem with a Grille to the smoke detectors...
#1 problem with designs from architects and engineers:
Lack of compliance with section 505 of the IECC. Almost every single State in the Union has agreed to comply with energy requirements from the federal government and the IECC applies is most cases. In our state, it always applies. I reject more electrical drawings for this reason.
#2 on printed drawings: Not specifying conductor insulation and conduit type. Just labeling the drawings as #4 Cu in 3" conduit does not help me to do fill calculations.
During my 37 years of working mostly from engineered drawings we didn't see that many problems. We got paid to put it in, paid to take it out or paid to fix it. I don't have any complaints at all, some things just can't be avoided.
I have a job checklist I usually try to run through before I send out a set of drawings. A few things to check:
1. Did the legend get put on the drawings? (I don't think I have ever sent out a set without one, but I frequently don't notice we don't have a legend until the project is almost complete.)
2. Running 500 kcm wire from a transformer to a 400 A breaker. Or (2) sets from a transformer to a 800 A breaker. Or (3) sets to any 1200 amp breaker.
3. Not getting two emergency lamps over the exterior doors.
4. Architects like to flip the door swings at the last minute, and not tell anyone. Guess whose fault it is when the light switches wind up behind the doors.
5. Always show doors on the lighting plan (see number 4 above).
6. Make sure an important layer isn't turned off at the last minute. (ie: drawings go out without any smoke detectors shown).
7. I always make a note to field verify any equipment requirements. There are frequently minor changes in their requirements that nobody can know about until long after the drawings are out.
8. I always make a note to coordinate all outlet locations. Things get changed (even after the drawings go out), and I always get blamed when the contractor puts an outlet behind a cabinet.
Steve
Without reading the whole thread, I'm gonna throw this one out:
Many commericial buildings have Men & Womens' restrooms. Usually, a SP switch is installed in each (or an occupancy sensor) to turn the lights on and off.
Seems no EE that designs the buildings I wire can understand that if you use circuit LB12 for the mens room, and circuit LC26 for the womens, you cannot take those two circuits to the same exhaust fan.
When I present this problem to the designer/engineer, they simply say to rewire the switches to 3-ways.
What further compicates the matter is when there's a third restroom for "Family".![]()
Not in any particular order:
1. Conduit fill and conductor derating.
2. Arc Flash/Short Circuit Current Rating.
3. Not using devices within the manufacturer's specifications, especially supplementary OCPD's.
4. Grounding of cabinets downstream of an isolation transformer.
5. Conductors undersized per the upstream fuse.
6. Lack of OCPD co-ordination.
...and my personal pet peeve of the week...
7. Not reading the manufacturer's manual until after the design was completed and their product is sitting on the shop floor.
I attached a wiring diagram for restroom fan lights and common restroom exhaust. Our biggest issue lately is the 277V lights and 120V exhaust fan. Yes, the restrooms are generally on the same power circuit ... but that doesn't matter with this setup. Thoughts?
This wiring diagram was being used in this office when I started here ... I haven't had any personal contractor reactions to it yet.
I agree, IECC (or ASHRAE 90.1) compliance is probably the one thing I tend to forget. Funny thing ... last job that I submitted I had done it ... and forgot to submit it with the drawings! <shaking head> At least that was a REALLY easy correction response item!
Running 500 kcm wire from a transfromer to a 400 A breaker. Or (2) sets from a transformer to a 800 A breaker. Or (3) sets to any 1200 amp breaker.
You have me confused here. These are good things or bad things?
Common excuse - but often the sprinkler plan is several months or more older than all other revisions of other RCP's - available to everyone and changes little after plan review.... Yet it takes two Foremen <5 minutes on site to realize the conflicts on some large peices of paper, another hour or so to generate a copy and paste RFI for 20+ RFI's of the same topic and wording but location specific, and another 3 months or more to get someone to not bury their head in the sand about it???? When at some point after plan review of the sprinkler set - that layer can be added as backround during the numeous revisions post de facto. It can be done - I've seen it - it's just rare for some reason.... Otherwise - It becomes what I call Contractor Aided Design.... Or Build and then Design...We coordinate lights and HVAC grilles in-house, but sprinklers are performance spec'd. We don't locate heads, so we unfortunately can't coordinate their locations at design.
I attached a wiring diagram for restroom fan lights and common restroom exhaust. Our biggest issue lately is the 277V lights and 120V exhaust fan. Yes, the restrooms are generally on the same power circuit ... but that doesn't matter with this setup. Thoughts?
This wiring diagram was being used in this office when I started here ... I haven't had any personal contractor reactions to it yet.
most office buildings will have the bathroom ex. fan(s) controlled by the BAS (if there is one) one hour before employees arrive 'til one hour after they leave. The fan needs to be running non-stop in the men's room for sure.
Do you ever look at the HVAC plan and the sprinkler plan for the layouts in hallways for Grilles and head placements? Seems no one ever does.
Either one of two things happen everyones needs to be in the same space or there's no over head space to get by the HVAC main trunk in the hallway.
Then theres always seems to be some problem with a Grille to the smoke detectors...
We coordinate lights and HVAC grilles in-house, but sprinklers are performance spec'd. We don't locate heads, so we unfortunately can't coordinate their locations at design.
Common excuse - but often the sprinkler plan is several months or more older than all other revisions of other RCP's - available to everyone and changes little after plan review.... Yet it takes two Foremen <5 minutes on site to realize the conflicts on some large peices of paper, another hour or so to generate a copy and paste RFI for 20+ RFI's of the same topic and wording but location specific, and another 3 months or more to get someone to not bury their head in the sand about it???? When at some point after plan review of the sprinkler set - that layer can be added as backround during the numeous revisions post de facto. It can be done - I've seen it - it's just rare for some reason.... Otherwise - It becomes what I call Contractor Aided Design.... Or Build and then Design...
I think you missed my point about the revisions... If the sprinkler plan is dated 2008, and the last revision of lighting is 2009 - means there is no coordination between plans in the event of conflict... If you don't get too many RFI's about this - the client may have already made an economic decision about who'll sort it out for you...But I can't coordinate sprinkler head locations before you see the plans.
Honestly ... I haven't seen too many RFIs dealing with this coordination. The Fire Protection contractors I've had must've been good!
I have been guilty of all of that.
Some of the coordination issues have to be left to the contractor due to the "multiple manufacturer" requirement by many owners. Trip-current current curves can vary widely from manufacturer to manufacturer and there isn't any budget to do coordination for every possible combination in the spec.