Will someone please guide me to the section of the NEC that says that one tennant can not supply power to another. Thanks in advance.
Thanks but that's not it. The senereo would be having to install a house meter and separate all branch circuits to supply only one teneant. If common areas exist, the landoord is responsible for the "house electricity".I don't know if this is what you are thinking about, but try 230.3
Thanks but that's not it. The senereo would be having to install a house meter and separate all branch circuits to supply only one teneant. If common areas exist, the landoord is responsible for the "house electricity".
Still not what I'm looking for.240.24 (b)
Thanks Roger, that's it.....Look at 210.25(B)
Roger
Look at 210.25(B)
Roger
Can you post that? I'm on '05 it.'s not there
210.25 Branch Circuits in Buildings with More Than One Occupancy.
(A) Dwelling Unit Branch Circuits. Branch circuits in each dwelling unit shall supply only loads within that dwelling unit or loads associated only with that dwelling unit.
(B) Common Area Branch Circuits. Branch circuits required for the purpose of lighting, central alarm, signal, communications, or other needs for public or common areas of a two-family dwelling, a multifamily dwelling, or a multi-occupancy building shall not be supplied from equipment that supplies an individual dwelling unit or tenant space.
Can you post that? I'm on '05 it.'s not there
210.25 Common Area Branch Circuits
Branch circuits in dwelling units shall supply only loads within that dwelling unit or loads associated only with that dwelling unit. Branch circuits required for the purpose of lighting, central alarm, signal, communications, or other needs for public or common areas of a two-family or multifamily dwelling shall not be supplied from equipment that supplies an individual dwelling unit.
Getting a bit technical here, but it looks like those articles are just saying you can't have a branch circuit supplying two different dwellings, but it doesn't seem to prevent one panel feeding individual branch circuits to different dwellings so long as each branch circuit only serves the one dwelling.
I have no idea why someone would want to do that, but it seems it is allowed.
Comments?
"or loads associated with that unit"
Branch circuits in dwelling units shall supply only loads within that dwelling unit or loads associated only with that dwelling unit.
I don't see how this statement forces one to install an individual service for each dwelling unit, it just says you can't supply loads within or loads associated with different units from the same branch circuit.
If you had a panel in dwelling unit A, and ran a 20A branch circuit to dwelling unit B where it connected to receptacles in only unit B, you would have a branch circuit in A which is supplying load in B. That would be a violation.
Again, I don't know why anyone would want to do it (unless the landlord was willing to pay for all the electricity).
If you had a panel in dwelling unit A, and ran a 20A branch circuit to dwelling unit B where it connected to receptacles in only unit B, you would have a branch circuit in A which is supplying load in B. That would be a violation.
Yes it would, but what if the panel was on the outside of the building? I'm not trying to argue that you can do this, I'm just saying that this particular article does not prohibit it. I do believe there are other restrictions that won't allow it to be done, just not this article.
The section does not prohibit the presence of circuit B in unit A. It only prohibits the use of circuit B in unit A.
The panel can be common as long as the individual branch circuits are dedicated to only one unit per circuit.