Read it again:
210.25 Branch Circuits in Buildings with More Than One Occupancy.
(A) Dwelling Unit Branch Circuits. Branch circuits in each dwelling unit shall supply only loads within that dwelling unit or loads associated only with that dwelling unit.
A circuit for unit A can be run through unit B. It's presence is not prohibited. It can supply only loads in unit A.
Read it again, this way:
210.25 Branch Circuits in Buildings with More Than One Occupancy.
(A) Dwelling Unit Branch Circuits. Branch circuits in each dwelling unit shall supply only loads within that dwelling unit or loads associated only with that dwelling unit.
A branch circuit for A which is run through unit B, is IN dwelling unit B and supplying loads WITHIN dwelling unit A. That is prohibited by the plain language of the code.
If the intent was to prohibit a branch circuit from supplying loads in different dwelling units at the same time, it would have said that. But that is not how it is written. I think the intent was to avoid having to enter one dwelling unit in order to open branch breakers for another dwelling. But the language also prohibits the circuiting (not just the branch breaker) from being in a dwelling unit for which it does not supply loads.