Re: What color is a 208 hi-leg ?
Originally posted by dduffee260:
If you have a 120/240 delta system with the 208 hi-leg, what color is this wire supposed to be. Some POCO's say it is orange. But would this not colflict with the 480 setup? Would you use a blue with orange tape also? How do you other guys color this phase?
110.15 requires that the high-leg be marked orange when the neutral is present.
There are no requirements for BOY or BRB. They are accepted norms and not enforced by the NEC. You should verify voltages with a meter.
Regarding a high leg, the other requirements are found in 215.8, 230.56, and 408.3(E).
In 408.3(E), note that the high leg is to be the "B" phase, unless the POCO has connected to a different point in the same enclosure. POCO's often put the high leg on the "C" phase, and mark it red. After that point, the high leg should be landed on the "B" phase. Personally, I have identified conductors in the meter "Black, Blue, Orange" at the service, and then "Black, Orange, Blue" at locations beyond that, but I'm not sure if that's consistent with established norms.