First, the bond is the appliance cabinet to the neutral, allowing the neutral to provide grounding, not the other way around, so the neutral must be a wire installed to neutral requirements.If an installer comes out to a house with a new 4 wire stove and the house only has a 3 wire se cable. Then he just puts a 3 wire cord on stove and barely bonds the neutral to the ground screw whats the worst that could happen??
I'm going to ruin the anticipation here. Here is what happened. I got a call for a new stove that "blew up with flames coming out back and large booms"! So off I went. Here is what I discovered.
Burn marks all over blower motor under stove
Melted 3 prong stove cord (just 12"-24" section) this was part under the stove on top of motor housing
Melted motherboard and capacitor on stove
Bonding strap was attempted to be put on green screw but someone skinned it and tried wrapping but barely even touching green screw with most threads melted but on a couple left with burn marks around green screw
Totally melted stove cord right in middle with conductor exposed
On 40 amp 2 pole federal pacific 40 amp breaker that eventually tripped
Stove worked for about 2 months then the above happened
Pics coming...
Ran new 6/3 and 4 prong 50 amp outlet
The loose bonding screw/strap was not the cause of all this, the result maybe, but not the cause. That's if the grounded conductor was landed in the neutral terminal on the stove. There had to be a fault to the frame and the loose bonding connection caused a high resistance resulting in the heated/burnt items in the path. Also why the breaker didn't trip when the fault occurred.
Was power supply cord neutral conductor landed on "neutral" or "appliance frame" side of the bonding jumper? Was "neutral" end of bonding jumper connection tight?I'm going to ruin the anticipation here. Here is what happened. I got a call for a new stove that "blew up with flames coming out back and large booms"! So off I went. Here is what I discovered.
Pics coming...
Presuming the supply cord conductor(s) was anything between 10 AWG and 6 AWG, I don't see enough current flowing, especially as a result of open neutral issues, to get it hot enough to melt the cord, unless there was short circuit or ground fault current flowing and OCPD failed to open in timely manner. You did mention it was a FPE breaker.
Obviously, the damaged cord energized the cabinet.
And possibly put 240V across a 120V control board (compromised neutral).Obviously, the damaged cord energized the cabinet.
photo..