When we take any brand overload device and place it on an 80 or above percent constant load it will show signs of failure. Take that 15 amp single pole FPE breaker and load it to 50 percent and it will last the lifespane of the average house.
yeah, that 15 or 20 amp residential breaker that nuisance trips has been
running at 90%, for years. after a while, they just get cooked.
for that matter, ambient temperature is a consideration, and double breakers
filling a panel are notorious for nuisance tripping, just cause of the density
of heat generating breakers present.
i had a 15 amp breaker that wouldn't hold past about 10 amps, and there
were doubles on either side, well loaded. it was hot to the touch, with nothing
loading it.
friend of mine in phoenix has his house panel on the sunny side of the house,
(as if there is a side of phoenix that isn't sunny)... he calls and says he has
breakers tripping all the time.... and the electrician he called said his panel has
to be upgraded...
before we did that, we put something shading the panel.... problem magically
disappeared....