If I apply a 30 amp load to a 20 amp breaker and it trips within a minute or two, it tells me that the breaker is working properly. How is that not a legitimate test?
but is the breaker tripping due to the overload? Or is it tripping because the connection to the buss is heating up, and out of the panel the breaker might not trip on 30a?
To the OP, another thing I forgot to mention -you touch a panel and you own it. You take wires off breakers to connect yout test setup, the breakers trip on overload so the owner does nothing. But you unknowingly disturbed some breakers where the stab was barely making contact because it was burned behind the breaker. A week later the panel burns up, guess who is paying for the owners new service.