There is copy of 2018 70E I have access to at work, I have just never personally read it yet or had any recent training on it that I was awake for.
I made a copy of that form yesterday.
Just leads to more questions...
For the Troubleshooting that's permitted what PPE do you use for voltages over 300V in the example scenarios above?
What about DC? Say 440 -500V solar PV strings coming into a PV inverter, and the service electrician is removing the cover of the inverter to check string voltage? Probably not much AF current in the DC but still over 300V.
Thanks
You should use the latest copy of 70E because it's a National Consensus Safety Standard (NCSS) and as such includes safety improvements with each edition. It's also what legal jurisdictions use, the latest edition of any NCSS. Get it with the Free Access method at NFPA.org. But, if you're just looking for the EEWP, I don't think it changed in the 2021 edition.
The EEWP will have you do Shock and Arc Flash assessments and as part of the Shock assessment you'll select rubber gloves for under your leathers from the Glove Classes that vary from ASTM Class 00 to Class 4. Class 00 works for the applications you're describing. For the Arc Flash assessment you use either the incident energy (IE) calculations or the 70E Categories method for determination of the appropriate PPE. The Categories method though is limited in what it applies to in terms of available fault current and the PPE only goes to PPE 4 which is 40 calories.
What's required for the IE calculations is the Utility contribution and ocpd, and the electrical model up to the point you're interacting with. It's typically done using power systems software for Fault, Coordination and Arc Flash calculations. I think it would be a good hustle for an electrician to partner with an engineer to do Arc Flash Studies. In my estimation, over half of the work associated with an Arc Flash Study is data collection, and all that could be done by an electrician.
And one final comment on the state of the NFPA 70E standard. I took a 16-hour virtual class recently on 70E. I found out from the trainer, who is very qualified and well-versed at the Standard, that installation of Power Quality monitoring equipment would always require an EEWP. Her contention (yes she was a lady, and fine at that) was that coming in contact with insulated cable is the same as coming in contact with uninsulated bus. This caught me by surprise because we routinely open panels and install recording CT/meters for demand information. Fortunately as it turns out the last two clients were a hospital and an NIH building so they readily signed EEWPs.
I was also paranoid about the data collection we do for Arc Flash Studies, whether she would balk at that. But for that application, the only requirement is that you be suited to cover the Incident Energy.
Good luck.