I've found a befuddling little wormhole. 310.12 states:
For a service rated 100 amperes through 400 amperes, the service conductors supplying the entire load associated with a one-family dwelling, or the service conductors supplying the entire load associated with an individual dwelling unit in a two-family or multifamily dwelling, shall be permitted to have an ampacity not less than 83 percent of the service rating.
That's all well and good, but it bothers me that "service rating" is not defined anywhere in the Code. We all probably think we know what the service rating is, but what is it really? A few options:
Maybe it's the calculated load from 220? I don't really believe that since the service can be bigger than the calculated load. However, this is supported by an example in Informative Annex D, where the service rating is equated with the calculated load:
Example D2(b) from 2023:
Calculated Load for Service
29,200 VA ÷ 240 V = 122 A (service rating)
Maybe it's the minimum conductor ampacity required by 230.23, as informed by 310? If that's the case, Table 310.12(A) should really reference the calculated load instead of the "Service or Feeder Rating". Otherwise we have a circular logic situation where 310.12 is saying the ampacity of the service is 83% of the ampacity of the service.
Maybe it's the service disconnect OCPD rating? This is what most people would say and what I think is likely the correct answer, but it still seems murky and could be made more explicit. Undefined terms like "service rating" should either be defined or discarded.
Maybe it's whatever the utility says the service is or whatever the available increments of utility service are? That interpretation is kind of supported by looking at Example D7 in Informative Annex D:
"If a 175-ampere service rating is selected, a service conductor is then sized as follows... 175 amperes × 0.83 = 145.25 amperes per 310.1"
A service rating is "selected", not "calculated", so perhaps it's selected based on the utility's stated service ampacity?
I'm interested to read what other people think. Maybe there's something obvious that I'm overlooking.
For a service rated 100 amperes through 400 amperes, the service conductors supplying the entire load associated with a one-family dwelling, or the service conductors supplying the entire load associated with an individual dwelling unit in a two-family or multifamily dwelling, shall be permitted to have an ampacity not less than 83 percent of the service rating.
That's all well and good, but it bothers me that "service rating" is not defined anywhere in the Code. We all probably think we know what the service rating is, but what is it really? A few options:
Maybe it's the calculated load from 220? I don't really believe that since the service can be bigger than the calculated load. However, this is supported by an example in Informative Annex D, where the service rating is equated with the calculated load:
Example D2(b) from 2023:
Calculated Load for Service
29,200 VA ÷ 240 V = 122 A (service rating)
Maybe it's the minimum conductor ampacity required by 230.23, as informed by 310? If that's the case, Table 310.12(A) should really reference the calculated load instead of the "Service or Feeder Rating". Otherwise we have a circular logic situation where 310.12 is saying the ampacity of the service is 83% of the ampacity of the service.
Maybe it's the service disconnect OCPD rating? This is what most people would say and what I think is likely the correct answer, but it still seems murky and could be made more explicit. Undefined terms like "service rating" should either be defined or discarded.
Maybe it's whatever the utility says the service is or whatever the available increments of utility service are? That interpretation is kind of supported by looking at Example D7 in Informative Annex D:
"If a 175-ampere service rating is selected, a service conductor is then sized as follows... 175 amperes × 0.83 = 145.25 amperes per 310.1"
A service rating is "selected", not "calculated", so perhaps it's selected based on the utility's stated service ampacity?
I'm interested to read what other people think. Maybe there's something obvious that I'm overlooking.