Total tangent, but why no microwave or disposal?Wyane I am sorry I have to disagree thats still not how you do a 220.85 Two dwelling calc.
To arrive at your 95A optional take the following:
Total tangent, but why no microwave or disposal?Wyane I am sorry I have to disagree thats still not how you do a 220.85 Two dwelling calc.
To arrive at your 95A optional take the following:
It is, you are mistaken.Wayne I am sorry I have to disagree that's still not how you do a 220.85 Two dwelling calc.
These are made up examples to illustrate a point, so if it's convenient, we can leave out appliances that while common are not actually required to be in every dwelling unit.Total tangent, but why no microwave or disposal?
Post your proof of work I already posted mine.It is, you are mistaken.
You're getting closer to my example, notice that 194A > 2 * 95A, so already there's a disparity, just not quite enough to be an issue once you round up to standard breaker sizes.
But I specified 15A of HVAC load. So change the HVAC to just one heat pump at 15A / 3600 VA. And to get the 220.82 load back to 95A, add another appliance of 3440 VA.
Now when you do the 220.85 calculation, you'll get a 2-unit load of 206A.
Cheers, Wayne
But it says "For a X, the Y, or the Z, blah blah". That lack of parallelism in the articles indicates that the first reading you suggest is not correct. As does the context.I can see this interpretation, but the "For.... X, Y, OR Z" can also be read as "For X, for Y, OR for Z" rather than "For all X that are Y or Z."
I already posted sufficient information for you to verify the computations, but since you asked, I'll update your very nice tables to facilitate that.Post your proof of work I already posted mine.
| Single dwelling unit feeder 220.82 | | | VA | |
Line | Description | VA | QTY | VA | Neutral |
1 | General Lighting Load | | | | |
2 | Apartment square Feet | 3 | 1747 | 5241 | 5241 |
3 | Small Appliance | 1500 | 2 | 3000 | 3000 |
4 | Laundry | 1500 | 1 | 1500 | 1500 |
5 | Water heater | 4500 | 1 | 4500 | 0 |
6 | Dishwasher | 960 | 1 | 960 | 960 |
7 | Electric Clothes Dryer | 5000 | 1 | 5000 | 3500 |
8 | Range | 11000 | 1 | 11000 | 7700 |
9 | Microwave | 1800 | | 1800 | 1800 |
10 | | | | | |
11 | Sub Total | | | 33001 | 23701 |
12 | | | | | |
13 | First 10 kva | | | 10000 | |
14 | Remainder | | | 23001 | |
15 | 40% of remainder | | | 9200 | |
16 | | | | | |
17 | | | | | |
18 | Ductless Heatpump | 3600 | 1 | 3600 | 0 |
20 | | | | | |
21 | Total | | | 22800 | |
22 | Amps | | | 95 | |
| Two dwelling units NEC 220.85 | | | | | | |
| 220.84 Multi family | | | | | VA | |
Line | Description | VA | QTY | NEC Section | | Phase | Neutral |
1 | General Lighting Load | | | | | | |
2 | Total square Feet | 3 | 3492 | 220.84(C)(1) | | 10482 | 10482 |
3 | Small Appliance | 1500 | 4 | 220.84(C)(2) | | 6000 | 6000 |
4 | Laundry | 1500 | 2 | 220.84(C)(2) | | 3000 | 3000 |
5 | Water heater | 4500 | 2 | 220.84(C)(3) | | 9000 | 0 |
6 | Dishwasher | 960 | 2 | 220.84(C)(3) | | 1920 | 1920 |
7 | Electric Clothes Dryers | 5000 | 2 | 220.84(C)(3) | | 10000 | 7000 |
8 | Main House Range | 11000 | 2 | 220.84(C)(3) | | 22000 | 15400 |
9 | Microwave | 1800 | 2 | 220.84(C)(3) | | 3600 | 3600 |
10 | Ductless Heatpump | 3600 | 2 | 220.84(C)(5) | | 7200 | 0 |
11 | Sub Total | | | 220.84(C) 1-5 | | 73202 | 47402 |
12 | | | | | | | |
13 | Multiply Line 11 by 150% to make 3 'dummy’ units | | 1.5 | 220.85 | | 109803 | 71103 |
14 | | | | | | | |
15 | Apply 45% Demand Factor For Total Load | | | T220.84 | | 49411 | 31996 |
16 | | | | | | | |
17 | Amps | | | | | 206 | 133 |
Maybe next time you'll believe me when I say I'm not doing that.Ok yeah I see what you mean, I just wanted to make sure you were not using 220.82 as an input to 220.85.
You can't use 220.82 for a duplex, its only allowed for one dwelling unit.you can just add up the results of 220.82.
We've had this disagreement before, and my example above shows why that interpretation is non-sensical. That interpretation says a 200A service to a panel containing only two 100A breakers is a violation, that the service would need to be at least 205A.You can't use 220.82 for a duplex, its only allowed for one dwelling unit.
Its not so much that I disagree your logic is good, its that if I use that on a plan submittal I get red lined and turned down, I have had conversations with AHJ's on it and they are unmoved, so I think its misleading to say people can use it unless your a practicing EE and get it approved on your plans.We've had this disagreement before,
Is your experience of that happening in Oregon only?Its not so much that I disagree your logic is good, its that if I use that on a plan submittal I get red lined and turned down,
Yeah I only work Oregon at present, there are a ton of ADU's going in now so it comes up often.Is your experience of that happening in Oregon only?