I try for 46 to center and try to get all devices at same around the space Switches etc. I too like the laser level to line up all boxes. Regardless of preference the code does have a requirement, so knowing finished height of countertop is important.
(2023 NEC) 210.52(C)(3)(1)
(3) Receptacle Outlet Location.
Receptacle outlets shall be located in one or more of the following:
(1)On or above, but not more than 500 mm (20 in.) above, a countertop or work surface
Also a work surface that might be placed lower than "normal" for ADA compliance in specific installation the above can force you to put it lower over the countertop/work surface than the light switches not at the countertop.
Nothing worse that getting everything installed and have to go back and move because someone decided to or to level the counter ended up higher than expected (been there). Or design changes from a stone counter to a Formica with integrated backsplash.
How many have come back after rough-in to find a full height cab covering the receptacle location or the tiler had covered the box location without making full cutout and tile was a surprise because not part of original plan and now box is recessed?