oops typo 14/4I'm afraid I don't see how, unless you do different routing of the 3-ways.
Mark
oops typo 14/4I'm afraid I don't see how, unless you do different routing of the 3-ways.
Mark
You can wire 3-ways through a chain of multiple lights with it - travelers and neutral going, switch leg coming backI think it could also be used for 3-way switching where the new code rule requires the neutral be brought to the switch. It would be 1 Hot, 2 Travelers and 1 Neutral.
Mark
Yes. I'm not fully seeing the use for X/2/2. It's more than twice the price of X/2. I've never actually seen it in the wild, even in new construction.That could be accomplished via a 14/3 also.
X/2/2 not necessary for switch locations perse X/3 would suffice, but with the residential use of AFCI breakers mandatory in most applications, MWBC not functionally useful with most AFCI on market forcing the EC to install individual runs of X/2 for each branch circuit. X/2/2 allows for a single pull to give 2 branch circuits with one pull. Cost/Benefit ratio might not always be there depending on complexity of the pull. I have used the X/2/2 for that reason when blind pulls between levels or spaces would become to complicated or intrusive to run multiple single pulls.Yes. I'm not fully seeing the use for X/2/2. It's more than twice the price of X/2. I've never actually seen it in the wild, even in new construction.
To comply with code, there only needs to be a neutral in ONE switch location. Just supply the power from there and run X/3 around.
I'm not seeing that in the 2017 code. Has something changed?Yes. I'm not fully seeing the use for X/2/2. It's more than twice the price of X/2. I've never actually seen it in the wild, even in new construction.
To comply with code, there only needs to be a neutral in ONE switch location. Just supply the power from there and run X/3 around.
404.2(c) says you have to provide a grounded conductor for controls. But if you can see the entire floorspace of an area from the switches, you only need at one switchI'm not seeing that in the 2017 code. Has something changed?
Mark
Another instance of stupid code. Just make a neutral required at every switch location unless there is a raceway where if needed it can be added later. There is no reason why the NEC needs to make this so complicated.404.2(c) says you have to provide a grounded conductor for controls. But if you can see the entire floorspace of an area from the switches, you only need at one switch
Yeah, they took the long way around the barnAnother instance of stupid code. Just make a neutral required at every switch location unless there is a raceway where if needed it can be added later. There is no reason why the NEC needs to make this so complicated.![]()
Correction: Some AFCI's do not support MWBC. Early AFCI's pretty much none did though. Once they found ways to pass listing without a GFP component, those that went that way will work on MWBC's, or a two pole AFCI is an option that wasn't always there either.Solves the issue of running two 120V circuits that used to be done with a 3 wire cable and a MWBC. AFCI does not support MWBC. Also can be used for 2 GFCI circuits without paying the big price for 2-pole GFCI.
Mark
A grounded conductor has been required since the 2011 code cycle.I'm not seeing that in the 2017 code. Has something changed?
Mark