Actually I do see an advantage for "sensitive electronic equipment" to operates at 60/120V. With all loads connected L-L, lower voltages to ground may lead to less interference.That said, I believe that these systems are band-aids to fix devices with poorly designed power supplies and poorly designed ground referenced signal cables.
I just have a problem using the generic term "Balanced Power" when a specifically defined term is more appropriate.
I do not know how many times I have seen people simply specify an "isolation transformer" for an electronic load and then be disappointed that the supplied unit was not a K-rated constant voltage device with triple shielding. Short-cut and slang phrases often lead to problems when "outsiders" happen into the conversation.