- Location
- Lockport, IL
- Occupation
- Semi-Retired Electrical Engineer
I am designing a 150 room dormitory building. Each room will have two beds, two closets, and a shared bathroom. Each room is going to have a microwave oven to which I plan to assign a load of 1kW. I am looking for a way to not have to include 150kW just for microwaves in the service load. At the present stage of the design, we are treating the outlets for microwaves as being just a receptacle (but with 1000 VA instead of 180 VA), and including them in the “50% after the first 10K” demand factor. But whether we have other options depends on how we treat the microwave.
I prefer the answer to #1 to be “no,” because I don’t want to call this building a multi-family dwelling unit. I might be able to justify a “yes” to #2 by saying this is “other kitchen equipment” that has intermittent use. But that gives me no better than a 65% demand factor. I can get a lower calculated load if the answer to #3 is “no.” One key difference between #1 and #3 is the word “permanent.” This word appears in the definition of dwelling unit, but not in Table 220.42.
But here is my real dilemma. That table is for lighting, but we can use it for receptacles that we calculate using 220.14(I). That article says “not less than 180 VA,” and 1000 VA is certainly not less than 180. But if I know that the intent is to plug a microwave into a certain receptacle, does that put me into 220.14(A)? If so, then I think I cannot use the demand factors in Table 220.42.
Comments?
- Is it, for example, “permanent provisions for cooking,” in the context of the definition of “dwelling unit”?
- Is it rather “kitchen equipment,” in the context of 220.56?
- Would it disqualify us from using Table 220.42 because our dorms are not “without provisions for cooking by tenants”?
I prefer the answer to #1 to be “no,” because I don’t want to call this building a multi-family dwelling unit. I might be able to justify a “yes” to #2 by saying this is “other kitchen equipment” that has intermittent use. But that gives me no better than a 65% demand factor. I can get a lower calculated load if the answer to #3 is “no.” One key difference between #1 and #3 is the word “permanent.” This word appears in the definition of dwelling unit, but not in Table 220.42.
But here is my real dilemma. That table is for lighting, but we can use it for receptacles that we calculate using 220.14(I). That article says “not less than 180 VA,” and 1000 VA is certainly not less than 180. But if I know that the intent is to plug a microwave into a certain receptacle, does that put me into 220.14(A)? If so, then I think I cannot use the demand factors in Table 220.42.
Comments?