roger said:This might be fine for a small building, but a large facility that has a color or marking already established ( I have been in mills and factories that have used Blue, Red, and even Purple) should not have another color introduced (added) into the system.
Roger
I agree about the large already established facility not changing their color code but I think you would still have to fall back to the ?effective? wording of 110.15.
The most common color code in use is black, red, blue for systems 120v to ground and brown, orange, yellow for 480v systems [straight 240v deltas vary by contractor and/or area in the country]. . According to that practice, the high leg 120/240 delta is usually coded black, orange, blue with the B phase the high leg.
This being the usual practice, which of the following phases would be assumed as the high leg ?
Minuteman said:Here too. Except the panel I was in last week. It was marked A (blue) B (yellow) C (red)
I would think yellow is the ?odd ball? and yellow is the B phase so therefore most likely the high leg. . But that didn?t prove to be the case
Minuteman said:Here too. Except the panel I was in last week. It was marked A (blue) B (yellow) C (red) with C as the high leg.
It wouldn?t be reasonable to require a change in a large established facility but it should be otherwise marked ?by other effective means?. . Some type of marking should be added if the original chosen route isn?t ?effective?.
David